For one thing, if just the outside unit was replaced, how do we (you) know it is compatible with the indoor system, in particular the evaporator coil. Depending on how old the evaporator coil is, the outside unit (minimum 13 SEER) may not match up to achieve its rated sensible and latent BTU capacity and efficiency. Does the evaporator coil have a fixed orifice metering device or a thermostatic expansion valve (like it should)?
The other thing is if the indoor blower and evaporator coil were really dirty (dirty enough to affect the operation of the system), a good technician would be able to tell there was a problem when he was charging the system with refrigerant. If they measured dry bulb and wet bulb temperatures, took superheat or subcooling temperatures, they would know the blower and evaporator coil were dirty when they installed the condensing unit.
Unfortunately, there are many "technicians" in this trade who aren't as skilled and knowledgeable as they should be and it appears your contractor may have hired the "low bid" HVAC contractor to replace the condensing unit.